[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑 3 L6 \" o/ `  a! a

+ V, I) C' k  ^9 u- x' oWe all know that if you want to change the rotation of a three  phase AC motor.) S# s# @5 n3 I8 i& E0 u
Just swap any of the two phase leads.
! J# O8 S- h- w8 GBut for VFD application you need to do the swap after the inverter.3 _. W- Z4 J$ W* S
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
6 K) q) e% f5 h% }6 A: w5 g5 o  S' Z& t  {
As the principal of the VFD works, bascially from AC to DC, then DC to AC. & }2 E" q7 u3 p3 f, T  D+ g- ?
: C/ z( k; z+ Y1 ?. ?9 F( ?
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
0 j. W2 G8 }- ?- t& K$ l9 a
, H0 ^6 n2 d. B1 _5 OThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.