We all know that if you want to change the rotation of a three  phase AC motor.
. a' V) i9 u  D5 CJust swap any of the two phase leads.1 Z5 N# s2 X& t$ k# H2 j
But for VFD application you need to do the swap after the inverter.
# L$ J; G% P( pIf you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.8 G. @4 a% n" t
9 V; ^8 b+ r& a  b+ a( h
As the principal of the VFD works, bascially from AC to DC, then DC to AC.   s  K+ K- u5 Z) y4 V4 m$ M

4 P" {6 ^8 Y; R' I5 J  G+ v- A8 X# D$ ^The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
5 q4 c$ b( U0 h: Q3 c- p, z& K& D( Z. \2 U
The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.