Two cutler –hammer advantage starters are doing the same thing:8 |9 q x; l5 C& n8 ]5 ^
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
9 @ ]1 Q% U0 T! ZIt is a cycle.4 D7 l9 T+ a( R/ q
2 a# N( I/ ~8 Y$ u
We isolate the network control and use the local start and stop only, the problem remains.
7 I0 Y, G; y9 ^, O7 TSwap one of the defective buckets with a good one, the new bucket works fine.
7 ^) K1 j4 `3 D0 R! j/ H/ `The problem should be inside the bucket.
4 k3 B8 U' H; R
, X5 S4 c7 Y8 @" S8 J qWhen the problem happened, we observed that the contactor has a pulling action but will not seal.: u6 W7 {' O* m& N3 E7 q8 }
Use a terminating screw divers to push in the contactor, it will not seal either.
. v) Q7 Z/ c: U( Q$ T: @6 RConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same./ X/ y5 |& R; d. v. m
0 L: ^/ i1 S) S( M) T) |7 S
The next thing we can think of is the coil, we took the coil out to have a close look.
2 c8 e& X% O- k, e2 U% U& xThey have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
1 w6 |7 A% K# e* F& ?6 n; H- u% B! z It is getting better this time, we have 7-8 times of running before it quit working.
9 x, j6 d9 a; ^
6 O% p/ U9 |% Y+ m- I9 PThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 0 `/ p# u1 ?" T h
5 m R) r- m8 J2 Q- \& V7 g: T, D
Do you guys have any input on this issue? |
|