30-400 Wiring of luminaires
/ j4 e1 M+ ?0 rAll electrical wiring on or within a luminaire shall be
7 ]) U" i; n% c$ ](a) neatly arranged without excess wiring;4 y$ u0 `6 u# h( D) b* V+ ^
(b) not exposed to mechanical injury; and& l, Z/ P! \5 V6 w
(c) arranged so that it is not subjected to temperatures above those for which it is rated." \7 J- r2 Y- C2 Z
30-402 Colour coding0 X: {/ j1 B* {" p
Notwithstanding the requirements of Sections 0, 4, and 10 with regard to the colours used for distinguishing and identifying conductors, a continuous-coloured tracer in the braid of an individual braided conductor shall be permitted for the supply conductors of a luminaire, the colour of the tracer being black, white, and green for the ungrounded, identified, and bonding conductors respectively.
' j! ?# _* y( {30-404 Conductor insulation
# q* g: ]1 ~1 o* ^3 \Luminaires shall be wired with conductors at least No. 18 AWG, having insulation suitable for the voltage and temperatures to which the conductors may be subjected.
$ |$ ~' ]9 D$ z8 L% G" H) o/ s& L30-408 Wiring of ceiling outlet boxes, d4 t$ O" a8 s8 M, [
(1) Branch circuit conductors having insulation suitable for 90 °C shall be used for wiring of ceiling outlet boxes on which a luminaire is mounted, except for boxes in wet locations where Type NMW or NMWU cables are used.
# t& c% u4 X {7 \/ s9 R6 D(2) For purposes of compliance with this Rule, the ampacity of 90 °C wire shall be limited to the ampacity of 60 °C wire. |
|