) c. }( L8 @8 q q8 }# B; \Two cutler –hammer advantage starters are doing the same thing:
2 G# p6 o" B* G q+ z After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
6 E$ F, f- r) O' N3 Q( MIt is a cycle.# R7 s6 U7 ^1 z# }" a4 C! Y5 m
) b0 p+ G1 D7 Z! v3 J2 Z2 r, j9 mWe isolate the network control and use the local start and stop only, the problem remains.
: u. U9 ? @+ i; DSwap one of the defective buckets with a good one, the new bucket works fine.+ A$ A5 j4 x2 \* K
The problem should be inside the bucket.
M; ^4 Q) H# V# r4 I* D' [: |; T9 s" n/ x. n
When the problem happened, we observed that the contactor has a pulling action but will not seal.. x6 D9 T/ b8 t, a# l/ n
Use a terminating screw divers to push in the contactor, it will not seal either.4 U4 V2 x$ C. s( P8 c% J; f5 ^( h
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
: B* o: t/ R5 O! P7 t, |
6 J. J0 u& f" B5 l1 s3 cThe next thing we can think of is the coil, we took the coil out to have a close look.% j, \, U( O/ V. c6 A
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
1 M2 C* V M; M3 e1 F7 j' g+ ^$ b It is getting better this time, we have 7-8 times of running before it quit working. " w+ ?, T( d, X+ X# j! ^$ u
+ l1 `! L* l& S8 c4 } f6 T, C j
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
1 S1 |' {8 I5 d7 w' [: ?
6 n- v* @6 y. F4 yDo you guys have any input on this issue? |
|