[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑 8 ]( ^" B5 O2 a3 L& R4 b6 g

2 u! V8 X5 z( z2 _& ~We all know that if you want to change the rotation of a three  phase AC motor.
& q4 o% [' x" A5 h, uJust swap any of the two phase leads.
  \' ]9 c( P6 j+ gBut for VFD application you need to do the swap after the inverter.# Z+ }- E5 i% v& b; `9 }; r
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
& Z4 |- `- b0 R" \+ h
' s2 P# V6 R# X* V( DAs the principal of the VFD works, bascially from AC to DC, then DC to AC.
* \2 S, ?+ W, K* v) J0 ?5 t
! L3 E& L- s1 @( h9 j5 L+ N2 ~# ]8 w' tThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.: J5 ^. {* w/ L

- s. `5 {5 P! g$ C* }8 F# u& JThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.