[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
本帖最后由 td456 于 2010-4-14 12:28 编辑 # x, \" t  t& {) K

: _: z' T! Y: t/ CWe all know that if you want to change the rotation of a three  phase AC motor.
% a  o" c, y7 |" _7 M2 p& [+ e- G; Y; IJust swap any of the two phase leads.
9 U2 B! V7 X- N2 cBut for VFD application you need to do the swap after the inverter.$ h. A% F/ d" x) P/ F* ~
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
- C) \9 P' @: o' P  f) x
* @- r$ [3 |, S& |" ^  cAs the principal of the VFD works, bascially from AC to DC, then DC to AC. 7 p: n3 S) T# s* \/ D! C5 m2 D
8 r8 B; y) h. I3 i2 d* ~
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.# V- y6 D& g! N2 E

9 c4 x! {2 ~9 E1 w! R) V5 [The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.