[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑
1 B' ^" u( q* Z
2 _8 @, A% A0 d: D  c4 O' dWe all know that if you want to change the rotation of a three  phase AC motor.1 j# h- P( N) N& \, b, e
Just swap any of the two phase leads.
& H: W1 {* H! ~1 e: t& zBut for VFD application you need to do the swap after the inverter.. a- m* {4 g# K* B" q
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.6 y4 ~! d# Z) f

9 o* H, c0 [* B6 hAs the principal of the VFD works, bascially from AC to DC, then DC to AC. $ P( S; y* m7 ?6 h4 t
* M7 _/ m3 o7 k+ @2 H
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.& Z& D% t, I. Z( F( G) \9 W1 z

/ R8 _- T# b) U9 a. f' O/ xThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.