Two  cutler –hammer advantage  starters are  doing the same thing:
. n- I! c% Y7 \" n) V( G+ J After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
8 q5 w5 }: N: `2 J# p; NIt is a cycle.1 N9 s  f* Y! n- f/ j
' I9 e- `4 O* L1 k
We isolate the network control and use the local start and stop only, the problem remains.0 `* j  z' I0 C8 ?: f: T
Swap one of the defective buckets with a good one, the new bucket works fine.
7 b0 @! z  r- V" H0 vThe problem should be inside the bucket.
; H1 M  I0 v7 |; m2 N0 q, l2 Q2 O  \
When the problem happened, we observed that  the contactor has a pulling action but will not seal.
3 T9 I) s1 ?% G: d' _8 ?1 {) ]Use a terminating screw divers to push in the contactor, it will not seal either.
6 F% H* ?& G* ^# v4 b- rConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.
. t# }7 V4 u  j# D; z3 B+ ^! s  e+ d4 @  J9 Z
The next thing we can think of  is the coil, we took the coil out to have a close look.
! B) A# b2 @) {" I( \1 iThey  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.. H0 V5 N. J* |% O# x
It is getting better  this time, we have 7-8 times of running before it quit working.
6 e4 k4 I; f6 V: V* N( J( D
# Z6 r! M' i5 oThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
! H8 w% ~2 a/ u1 i3 u. y- }" m, h' w: A: F2 H4 u7 O
Do you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 6 q2 M% p# G  G( J1 ?

3 d8 r0 _" L. |6 {9 n3 v  d中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
) ]0 ^5 |. R  sSince your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行 . z! o/ o- t# @% y5 q) z
也想到这一点,不过这是新装的设备。6 }/ G$ I# v: r& l! d; ?( x
检查过触点没问题。