[技术互助] Any input on Cutler-Hammer Starter?

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 12:56 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-3-26 14:14 编辑
/ z& b- }0 W& S/ F* J' D* u8 B
# ~" e) r9 t! r  b( e8 z/ ^Two  cutler –hammer advantage  starters are  doing the same thing:" ~- B- O. \6 m% J; d
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again. & I+ A& T4 s  u4 L
It is a cycle.
) e8 O/ H2 b4 f6 c/ @
! J/ Q" I& R+ t0 T& r" u* l2 HWe isolate the network control and use the local start and stop only, the problem remains.
# t: }! M' `$ w# F9 qSwap one of the defective buckets with a good one, the new bucket works fine.# |0 A7 V' q) f& F  ~7 t, c
The problem should be inside the bucket.- G) K* S7 X# A2 W  ?" A
$ M* X5 Q2 U: V
When the problem happened, we observed that  the contactor has a pulling action but will not seal.0 f% ~$ m; ]- p( _( W2 U
Use a terminating screw divers to push in the contactor, it will not seal either.
& F* l0 A5 M4 iConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.: ~. O% Y$ z! \& v

1 n- H3 G8 f3 E" W9 cThe next thing we can think of  is the coil, we took the coil out to have a close look./ t7 s. G  u- s) Q! F8 L; s+ V
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
: U. T5 g+ S8 ~4 H) J( Z It is getting better  this time, we have 7-8 times of running before it quit working. 4 i, J' U7 h0 @. J! ^
2 S4 J6 r+ C1 X) T0 x9 M
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. - T; @" [' P" I( }$ ^$ \* Z# `9 x

5 F' A5 ~, W% C" D$ CDo you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 # r6 _+ M' k% ?' y

4 F. H# T' X% l4 y中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
0 d7 d1 ^: ~1 x' _  b& e9 |, v/ FSince your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行 1 N8 }+ K3 w6 `- s; ?) o
也想到这一点,不过这是新装的设备。0 Y) D& N1 y$ f" X7 |5 |
检查过触点没问题。