Two cutler –hammer advantage starters are doing the same thing:
. n- I! c% Y7 \" n) V( G+ J After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
8 q5 w5 }: N: `2 J# p; NIt is a cycle.1 N9 s f* Y! n- f/ j
' I9 e- `4 O* L1 k
We isolate the network control and use the local start and stop only, the problem remains.0 `* j z' I0 C8 ?: f: T
Swap one of the defective buckets with a good one, the new bucket works fine.
7 b0 @! z r- V" H0 vThe problem should be inside the bucket.
; H1 M I0 v7 |; m2 N0 q, l2 Q2 O \
When the problem happened, we observed that the contactor has a pulling action but will not seal.
3 T9 I) s1 ?% G: d' _8 ?1 {) ]Use a terminating screw divers to push in the contactor, it will not seal either.
6 F% H* ?& G* ^# v4 b- rConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
. t# }7 V4 u j# D; z3 B+ ^! s e+ d4 @ J9 Z
The next thing we can think of is the coil, we took the coil out to have a close look.
! B) A# b2 @) {" I( \1 iThey have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.. H0 V5 N. J* |% O# x
It is getting better this time, we have 7-8 times of running before it quit working.
6 e4 k4 I; f6 V: V* N( J( D
# Z6 r! M' i5 oThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
! H8 w% ~2 a/ u1 i3 u. y- }" m, h' w: A: F2 H4 u7 O
Do you guys have any input on this issue? |
|