We all know that if you want to change the rotation of a three  phase AC motor.
/ X% e( M; o* `. ~$ r. x3 dJust swap any of the two phase leads.# g0 g2 ~, C  _6 t6 r0 V
But for VFD application you need to do the swap after the inverter.. G; Y4 S* s( E1 }; Z& u
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.9 X0 J( j/ u# ^/ @9 W7 s4 ]
/ N( x+ m! ~6 G$ o7 w6 \
As the principal of the VFD works, bascially from AC to DC, then DC to AC. 7 ~1 Q% U( I- Q7 {# x) S& s+ Q
$ ]/ B+ L; [; f8 S: [% [( O
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
% b& n( N' ?% U" W( m6 ?3 Z' E7 a% V
. B# n8 |4 k( F8 k  x7 M" p$ R& Z) `The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.