We all know that if you want to change the rotation of a three  phase AC motor.
( i  ?& S( e4 y9 D8 QJust swap any of the two phase leads.
8 }1 @# e5 V$ T  q* q1 j- mBut for VFD application you need to do the swap after the inverter.. _* K  W; Q( q% s0 I+ m' h5 e1 T
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
+ z6 q( [2 ~; C0 [. q3 h$ q/ g7 c8 S) \- I! |2 }
As the principal of the VFD works, bascially from AC to DC, then DC to AC.
% [3 C9 s0 S* C5 Y0 \2 X$ @7 ?5 ^( b9 }! h
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
0 q' f, _" }" y8 [0 Y& F9 s+ I$ J' t' ]; e4 l
The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.