[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑
  \) F6 j2 x5 f) b' S7 n, K: v; M) f  k
We all know that if you want to change the rotation of a three  phase AC motor.3 z1 r7 {. B9 \, f( f/ B; u
Just swap any of the two phase leads.
: U: o! B! ?5 \But for VFD application you need to do the swap after the inverter.0 t8 n6 }$ X1 [) ^
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
# y4 i/ P" v# s  ]" j+ F
" A' I9 L0 k  U. t2 z" EAs the principal of the VFD works, bascially from AC to DC, then DC to AC. - ?- o& x, c  @. B

; [5 \5 P2 }, mThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
+ w# }7 h! t0 H( |. u3 s' d
0 d9 u8 l. O! j: d2 f: pThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.
鲜花(0) 鸡蛋(0)
发表于 2010-7-4 00:19 | 显示全部楼层
老杨团队 追求完美