[技术互助] Any input on Cutler-Hammer Starter?

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 12:56 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-3-26 14:14 编辑
7 b1 v+ w% c: o5 \4 {+ ~1 y
# B1 P9 O5 X* ^9 q4 NTwo  cutler –hammer advantage  starters are  doing the same thing:
+ x7 S/ Z2 e( u4 |3 \9 s After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
# e+ R( Z* O0 _. t6 S! D" aIt is a cycle.
0 d, i$ n! y; o+ d
8 {9 K) r: S6 E+ o- w7 QWe isolate the network control and use the local start and stop only, the problem remains.& o" \6 K' I9 h
Swap one of the defective buckets with a good one, the new bucket works fine.
7 C- x- R7 U  t7 b7 `. l. V' xThe problem should be inside the bucket.
5 s: ~% T( x# F+ }" e1 Z
  R. A% C9 Y8 x8 k$ F/ U- IWhen the problem happened, we observed that  the contactor has a pulling action but will not seal.* t% @& b* v( [8 Z5 _7 b
Use a terminating screw divers to push in the contactor, it will not seal either." P2 l3 b9 b7 H: y/ r
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.7 j. j7 }  C; @4 |3 F& `
! [0 J5 M2 r& T  a; u, w+ v' v: o
The next thing we can think of  is the coil, we took the coil out to have a close look.
2 g- F/ @$ k: I- g; M3 M1 wThey  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
. N# r. c+ {. E& \7 M It is getting better  this time, we have 7-8 times of running before it quit working.   |! p4 E5 j& W' Y1 @. C. H
6 C& ]* U1 P2 l& G5 |
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
4 I5 R) P) G9 z- J
, P6 E+ K; U; [( iDo you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 * i" J  J* a- v) W- d4 O, w

, J/ Q: h6 \- J& f" _  ~中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
  G5 a8 k3 u& l7 M: s8 cSince your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
. W: j- I, g" L( G也想到这一点,不过这是新装的设备。; K. O; M/ W$ t# q
检查过触点没问题。